    Wires for Water Heater Melted

    Well yesterday my GF ran out of hot water in the shower. Looked into it and saw that the power wires are all melted. My Dad thinks a heating element is bad and was drawing too much current and made them melt. Sounds plausible but I have a feeling that the connections weren't the best (just wire nuts) and that caused increased resistance/heat. The breaker didn't flip.

    Would you guys just rewire it and see what happens? I am nervous to do this incase it overheats/starts a fire. At the same time I don't want to tell the owner of the house (my GF's dad) that he should just replace it based on a guess as to what is wrong.

    Any tests I can do with a multimeter or something?

    Thanks!

  2. #2
    The one. The only. verified
    Join Date
    Sep 2010
    Owner Since
    August 28, 2002

    Location
    SWPA
    Posts
    4,042
    Thanks
    182
    Thanked 699 Times in 529 Posts
    Lou, when I had some issues with my hot water tank I did a quick google to see how to do the proper tests. I was able to replace both the heating element and the thermostat based on what I found.

    [06-05, 19:29] OhioSpyderman: Brian, finding a woman is NOT the answer, you need to shop for a good VACUUM

  3. #3
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    2002

    Location
    West MI
    Posts
    314
    Thanks
    15
    Thanked 32 Times in 18 Posts
    Take resistance readings of the elements, use ohms law to find out current draw.
    Sounds like the wiring or breaker is not correctly sized. Typically it should be 10 gauge wire on a 30 amp breaker

    92 3000GT VR4
    Matt

  4. #4
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    ~2006

    Location
    Pittsburgh, PA/Wheeling, WV
    Posts
    867
    Thanks
    36
    Thanked 15 Times in 11 Posts
    Quote Originally Posted by stealthee View Post
    Lou, when I had some issues with my hot water tank I did a quick google to see how to do the proper tests. I was able to replace both the heating element and the thermostat based on what I found.
    I did a quick search and didn't find anything too useful but I was focusing on the melted wires. I'll have to take another look. Thanks!

    Quote Originally Posted by sublime_whatigo View Post
    Take resistance readings of the elements, use ohms law to find out current draw.
    Sounds like the wiring or breaker is not correctly sized. Typically it should be 10 gauge wire on a 30 amp breaker
    I just looked in the box and when I flipped 2 30A breakers (they were linked together) it turned off power to the water heater. Does that mean it is 60A since they are linked or did I just turn off a circuit unrelated to the water heater, too?

    Are the elements in series or parallel?

    Can I tell by taking the resistance if the elements are dead or will that just help me find the current draw?

    Also, do people normally use those plastic wire caps for stuff like this? Is there anything special about them or can I just get new ones if I decide to hook it back up? I am used to soldering everything in my car..

    Thanks a lot!

  5. #5
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    2002

    Location
    West MI
    Posts
    314
    Thanks
    15
    Thanked 32 Times in 18 Posts
    Sounds like you got the right breaker, yes its a double pole breaker, still 30 amps as it does not add up.

    The elements are parallel but not really since they go through the thermostat, the 2 elements should never be running at the same time.

    If you find the resistance of them you can use 240/R = less than 30 amps. Should be about 12 ohms. Make sure to disconnect the wires from the elements and leave water in the tank

    Plastic wire nuts are the most common way to hook them up, just make sure they are good and tight.

  6. The Following User Says Thank You to sublime_whatigo For This Useful Post:


  7. #6
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    ~2006

    Location
    Pittsburgh, PA/Wheeling, WV
    Posts
    867
    Thanks
    36
    Thanked 15 Times in 11 Posts
    Just checked and they are both 11.? (I only have my crappy multimeter here which has the last digit burnt out lol). So that should be under 30A. This was with the wires hooked up and water in the tank. I guess I'll go check again with the wires off. The wires are 10 gauge.

    Would you recommend just cleaning up the burnt wires and hooking it up again, making sure the connections are tight?

  8. #7
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    2002

    Location
    West MI
    Posts
    314
    Thanks
    15
    Thanked 32 Times in 18 Posts
    Ya just keep an eye on it, could of been a loose connection like you said. Loose = heat

  9. #8
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    ~2006

    Location
    Pittsburgh, PA/Wheeling, WV
    Posts
    867
    Thanks
    36
    Thanked 15 Times in 11 Posts
    Thanks a lot. You have a paypal addy I can send a little holiday cheer to ?

  10. #9
    Forum User verified
    Join Date
    Sep 2010
    Owner Since
    2002

    Location
    West MI
    Posts
    314
    Thanks
    15
    Thanked 32 Times in 18 Posts
    Thats not necessary, glad to help.

  11. The Following User Says Thank You to sublime_whatigo For This Useful Post:


  12. #10
    Forum User
    Join Date
    Sep 2010
    Owner Since
    2000

    Posts
    1,241
    Blog Entries
    2
    Thanks
    213
    Thanked 91 Times in 64 Posts
    I had an issue like this just a few weeks ago. only about 4 months old water heater. it was a loose connector in my case that caused the wires to melt I cut the melted wires and rewired it .
    Last edited by mb7050; 12-21-2013 at 07:14 PM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
  • History
  • Information
  • Groups
  • Events
  • Resources
3000GT/Stealth/GTO Information and Resources
Team 3S
3000GT / Stealth / GTO Information
daveblack.net